Page 1 of 1

Ethernet/IP Slave

Posted: 20 Apr 2018, 08:09
by jvp
Hello,
Is it possible to exchange strings with the Ethernet/IP module?

Thank you.

Re: Ethernet/IP Slave

Posted: 20 Apr 2018, 09:10
by volker
Please tell us more about your requirements: Exchanging a string with what kind of master? Is the master processing the string like any process data and thus there is no problem with cyclical data exchange ? Or do you want to implement some kind of event based message telegram exchange? The latter is difficult to implement in a cyclic based field bus protocol like Ethernet/IP.

Re: Ethernet/IP Slave

Posted: 05 Jun 2018, 17:21
by gambrinus
Can the Ethernet/IP slave be used to communicate with an Allen Bradley Controllogix system as an Ethernet/IP master? This may seem like a silly question, but to my knowledge, there are subsets of the Ethernet/IP industrial protocol. I'm not certain that just because two devices support Ethernet/IP, they will work together "out-of-the-box". Will it work with the CIP protocol? Thanks in advance.

Re: Ethernet/IP Slave

Posted: 07 Jun 2018, 15:08
by Mathias
Yes, the GW EtherNet/IP can be connected to a EtherNet/IP Scanner (master) like the Controllogix devices. The GW can be accessed with the CIP protocol. Data can be transferred with explicite messages and with IO connections. Of course you have to configure the scanner. You can use the EDS file to do that. The EDS file can be downloaded from https://www.kunbus.de/support.html.

Re: Ethernet/IP Slave

Posted: 07 Jun 2018, 20:59
by gambrinus
Thanks!

Re: Ethernet/IP Slave

Posted: 08 Oct 2018, 15:56
by jvp
Thank you. Connecting to Controllogix devices is what I had in mind.

Re: Ethernet/IP Slave

Posted: 10 Sep 2019, 07:13
by kapilv
Hi

I am trying setup a Ethernet/IP Gateway with a RevPi Connect+. I wanted to read/write DIO inputs and outputs over Ethernet/IP. Our software uses CIP communication to read/write to Allen Bradley PLC and we wanted to replace Allen Bradley PLC with the RevPi Connect+. Is there a way I can setup Ethernet/IP to Master/Slave with RevPI and read Bits, Words and String same way we used to read/write with AB PLC. Please reply asap.

Thanks!

Re: Ethernet/IP Slave

Posted: 12 Sep 2019, 16:57
by dirk
Dear kapilv, the Gateway Modules are all Slave Modules. Here is a tutorial about how to commission Ethernet/IP Modules: https://revolution.kunbus.com/tutorials ... rect=en_US
If you need the Master or Scanner functionality with Ethernet/IP then you may also use Codesys.

Re: Ethernet/IP Slave

Posted: 25 Sep 2019, 18:17
by kapilv
Dirk,

Thanks for replying and providing some inputs on this.
Definitely, I will check CODESYS.
Thanks.