Hi Luka,
We have communicated this topic several times on our platform:
It is absolutely okay and in no way any error if the CPU runs during high load condition into a down-clocking. The CPU Core's operating temperature is with low load at room temp between 50 and 60 °C. When you are using all 4 cores with high load it will rise up to 80 °C and then down-clocking is automatically started. Even with down-clocking the CM3 will have huge advantages over the CM1. Down-clocking will happen stepwise from 1.2 GHZ down to 600 MHz. With all 4 cores running on 600 MHz you will still have three times the power of a CM1.
In our climate tests we could run all 4 Cores at 100% load at 55°C ambient with 600 MHz.
To get optimum performance you need to follow the following rules:
1) Switch off GPU if not used
2) Do not use high current USB devices directly powered by RevPi Core but use a external powered hub instead
3) Use RevPi Core in upright position on a DIN rail. we do need the "chimney effect" (Stack effect) between lower and upper ventilation slits of the case. So do not lay the Core on a table.
4) If using multiple devices connected to the core via piBridge try to position those directly adjacent to the core which have the least power dissipation (DI instead of DO etc.)
5) In a cabinet please take care of cables running on top or under bottom of the Core. They should not block air convection through the ventilation slits.
Please note that the Broadcom SoC has 2 reasons for don-clocking to 600 MHz:
a) It is in idle state (lazy and not working hard) so it reduces the clock in order keep the Core as cool as possible.
b) Is is in a high temperature condition caused by high load and needs to reduce power dissipation by slowing down processes.
So if yoru Clock reading is 600 MHz it does mot of the time not mean that there is a high temp condition but it is more likely that it feels not being challenged
Hope this helps to clarify the temperature topic.