This is the contents of config.rsc. I have trimmed the unused bits to fit in the message limits of the website.
{
"App": {
"name": "PiCtory",
"version": "1.4.2",
"saveTS": "20190813140004",
"language": "en",
"layout": {
"north": {
"size": 70,
"initClosed": false,
"initHidden": false
},
"south": {
"size": 200,
"initClosed": false,
"initHidden": false,
"children": {
"layout1": {
"east": {
"size": 500,
"initClosed": false,
"initHidden": false
}
}
}
},
"east": {
"size": 70,
"initClosed": true,
"initHidden": false,
"children": {}
},
"west": {
"size": 200,
"initClosed": false,
"initHidden": false,
"children": {
"layout1": {}
}
}
}
},
"Summary": {
"inpTotal": 147,
"outTotal": 88
},
"Devices": [
{
"GUID": "0c948f4a-c846-049a-0199-5576c93eef55",
"id": "device_RevPiAIO_20170301_1_0_002",
"type": "LEFT_RIGHT",
"productType": "103",
"position": "30",
"name": "RevPi AIO",
"bmk": "RevPi AIO",
"inpVariant": 0,
"outVariant": 0,
"comment": "",
"offset": 0,
"inp": {
"0": [
"TEMP_MON",
"0",
"16",
"0",
false,
"0000",
"",
""
],
"1": [
"FAN_CP",
"0",
"16",
"2",
false,
"0001",
"",
""
],
"2": [
"FAN_SP",
"0",
"16",
"4",
false,
"0002",
"",
""
],
"3": [
"InputValue_4",
"0",
"16",
"6",
false,
"0003",
"",
""
],
"4": [
"TEMP_MON_STATUS",
"0",
"8",
"8",
false,
"0004",
"",
""
],
"5": [
"FAN_CP_STATUS",
"0",
"8",
"9",
false,
"0005",
"",
""
],
"6": [
"FAN_SP_STATUS",
"0",
"8",
"10",
false,
"0006",
"",
""
],
"7": [
"InputStatus_4",
"0",
"8",
"11",
false,
"0007",
"",
""
],
"8": [
"RTDValue_1_i04",
"0",
"16",
"12",
false,
"0008",
"",
""
],
"9": [
"RTDValue_2_i04",
"0",
"16",
"14",
false,
"0009",
"",
""
],
"10": [
"RTDStatus_1_i04",
"0",
"8",
"16",
false,
"0010",
"",
""
],
"11": [
"RTDStatus_2_i04",
"0",
"8",
"17",
false,
"0011",
"",
""
],
"12": [
"OutputStatus_1_i04",
"0",
"8",
"18",
false,
"0012",
"",
""
],
"13": [
"OutputStatus_2_i04",
"0",
"8",
"19",
false,
"0013",
"",
""
]
},
"out": {
"0": [
"OutputValue_1_i04",
"0",
"16",
"20",
false,
"0014",
"",
""
],
"1": [
"OutputValue_2_i04",
"0",
"16",
"22",
false,
"0015",
"",
""
]
},
"mem": {
"0": [
"Input1Range_i04",
"7",
"8",
"24",
false,
"0016",
"You must use wire bridges for current measurement!",
""
],
"1": [
"Input1Multiplier_i04",
"25",
"16",
"25",
false,
"0017",
"",
""
],
"2": [
"Input1Divisor_i04",
"20",
"16",
"27",
false,
"0018",
"",
""
],
"3": [
"Input1Offset_i04",
"-5000",
"16",
"29",
false,
"0019",
"",
""
],
"4": [
"Input2Range_i04",
"2",
"8",
"31",
false,
"0020",
"You must use wire bridges for current measurement!",
""
],
"5": [
"Input2Multiplier_i04",
"1",
"16",
"32",
false,
"0021",
"",
""
],
"6": [
"Input2Divisor_i04",
"100",
"16",
"34",
false,
"0022",
"",
""
],
"7": [
"Input2Offset_i04",
"0",
"16",
"36",
false,
"0023",
"",
""
],
},
"extend": {}
},
{
"GUID": "91b4bc4b-ddb1-1ac5-3f95-70f47acc5718",
"id": "device_RevPiAIO_20170301_1_0_001",
"type": "LEFT_RIGHT",
"productType": "103",
"position": "31",
"name": "RevPi AIO",
"bmk": "RevPi AIO",
"inpVariant": 0,
"outVariant": 0,
"comment": "",
"offset": 89,
"inp": {
"0": [
"MF1_TEMP",
"0",
"16",
"0",
false,
"0000",
"",
""
],
"1": [
"MF1_FLOW",
"0",
"16",
"2",
false,
"0001",
"",
""
],
"2": [
"MF2_FLOW",
"0",
"16",
"4",
false,
"0002",
"",
""
],
"3": [
"MF2_TEMP",
"0",
"16",
"6",
false,
"0003",
"",
""
],
"4": [
"MF1_TEMP_STATUS",
"0",
"8",
"8",
false,
"0004",
"",
""
],
"5": [
"MF1_FLOW_STATUS",
"0",
"8",
"9",
false,
"0005",
"",
""
],
"6": [
"MF2_FLOW_STATUS",
"0",
"8",
"10",
false,
"0006",
"",
""
],
"7": [
"MF2_TEMP_STATUS",
"0",
"8",
"11",
false,
"0007",
"",
""
],
"8": [
"RTDValue_1",
"0",
"16",
"12",
false,
"0008",
"",
""
],
"9": [
"RTDValue_2",
"0",
"16",
"14",
false,
"0009",
"",
""
],
"10": [
"RTDStatus_1",
"0",
"8",
"16",
false,
"0010",
"",
""
],
"11": [
"RTDStatus_2",
"0",
"8",
"17",
false,
"0011",
"",
""
],
"12": [
"OutputStatus_1",
"0",
"8",
"18",
false,
"0012",
"",
""
],
},
"extend": {}
},
{
"GUID": "6ad3c1a4-6870-3bf1-6d55-b9d991ba9dc0",
"id": "device_RevPiConnect_20171023_1_0_001",
"type": "BASE",
"productType": "105",
"position": "0",
"name": "RevPi Connect V1.0",
"bmk": "RevPi Connect V1.0",
"inpVariant": 0,
"outVariant": 0,
"comment": "This is a RevPi Connect",
"offset": 178,
"inp": {
"0": [
"RevPiStatus",
"0",
"8",
"0",
true,
"0000",
"",
""
],
"1": [
"RevPiIOCycle",
"0",
"8",
"1",
true,
"0001",
"",
""
],
"2": [
"RS485ErrorCnt",
"0",
"16",
"2",
false,
"0002",
"",
""
],
"3": [
"RPI_TEMP",
"0",
"8",
"4",
false,
"0003",
"",
""
],
"4": [
"Core_Frequency",
"0",
"8",
"5",
false,
"0004",
"",
""
]
},
"out": {
"0": [
"RevPiLED",
"0",
"8",
"6",
true,
"0005",
"",
""
],
"1": [
"RS485ErrorLimit1",
"10",
"16",
"7",
false,
"0006",
"",
""
],
"2": [
"RS485ErrorLimit2",
"1000",
"16",
"9",
false,
"0007",
"",
""
]
},
"mem": {},
"extend": {}
},
{
"GUID": "19d3324c-1e44-0dd3-c271-6f1c83a25a05",
"id": "device_ModbusRTUMaster_20180122_1_1_001",
"type": "VIRTUAL",
"productType": "24580",
"position": "64",
"name": "ModbusRTU Master",
"bmk": "ModbusRTU Master",
"inpVariant": 0,
"outVariant": 0,
"comment": "ModbusRTU Master",
"offset": 189,
"inp": {
"0": [
"HEATER_V_HB",
"0",
"16",
"0",
false,
"0000",
"",
""
],
"1": [
"HEATER_V_LB",
"0",
"16",
"2",
false,
"0001",
"",
""
],
"2": [
"Input_Word_3",
"0",
"16",
"4",
false,
"0002",
"",
""
],
"3": [
"HEATER_I_HB",
"0",
"16",
"6",
false,
"0003",
"",
""
],
"4": [
"HEATER_I_LB",
"0",
"16",
"8",
false,
"0004",
"",
""
],
"5": [
"Input_Word_6",
"0",
"16",
"10",
false,
"0005",
"",
""
],
"6": [
"Input_Word_7",
"0",
"16",
"12",
false,
"0006",
"",
""
],
"7": [
"INPUT_WORD_8",
"0",
"16",
"14",
false,
"0007",
"",
""
],
"8": [
"HEATER_P_HB",
"0",
"16",
"16",
false,
"0008",
"",
""
],
"9": [
"HEATER_P_LB",
"0",
"16",
"18",
false,
"0009",
"",
""
],
"10": [
"Input_Word_11",
"0",
"16",
"20",
false,
"0010",
"",
""
],
"11": [
"FAN_V_HB",
"0",
"16",
"22",
false,
"0011",
"",
""
],
"12": [
"FAN_V_LB",
"0",
"16",
"24",
false,
"0012",
"",
""
],
"13": [
"Input_Word_14",
"0",
"16",
"26",
false,
"0013",
"",
""
],
"14": [
"FAN_I_HB",
"0",
"16",
"28",
false,
"0014",
"",
""
],
"15": [
"FAN_I_LB",
"0",
"16",
"30",
false,
"0015",
"",
""
],
"16": [
"Input_Word_17",
"0",
"16",
"32",
false,
"0016",
"",
""
],
"17": [
"FAN_P_HB",
"0",
"16",
"34",
false,
"0017",
"",
""
],
"18": [
"FAN_P_LB",
"0",
"16",
"36",
false,
"0018",
"",
""
],
"19": [
"Input_Word_20",
"0",
"16",
"38",
false,
"0019",
"",
""
],
"20": [
"Input_Word_21",
"0",
"16",
"40",
false,
"0020",
"",
""
],
"21": [
"Input_Word_22",
"0",
"16",
"42",
false,
"0021",
"",
""
],
"22": [
"TEMP_SET_PT",
"0",
"16",
"44",
false,
"0022",
"",
""
],
"23": [
"Input_Word_24",
"0",
"16",
"46",
false,
"0023",
"",
""
],
"24": [
"Input_Word_25",
"0",
"16",
"48",
false,
"0024",
"",
""
],
"25": [
"TEMP_PV",
"0",
"16",
"50",
false,
"0025",
"",
""
],
"26": [
"Input_Word_27",
"0",
"16",
"52",
false,
"0026",
"",
""
],
"27": [
"Input_Word_28",
"0",
"16",
"54",
false,
"0027",
"",
""
],
"28": [
"OVER_HEAT",
"0",
"16",
"56",
false,
"0028",
"",
""
],
"29": [
"Input_Word_30",
"0",
"16",
"58",
false,
"0029",
"",
""
],
"30": [
"Input_Word_31",
"0",
"16",
"60",
false,
"0030",
"",
""
],
"31": [
"Input_Word_32",
"0",
"16",
"62",
false,
"0031",
"",
""
],
"32": [
"Input_Bit_1",
"0",
"1",
"64",
false,
"0032",
"",
"0"
],
"33": [
"Input_Bit_2",
"0",
"1",
"64",
false,
"0033",
"",
"1"
],
"34": [
"Input_Bit_3",
"0",
"1",
"64",
false,
"0034",
"",
"2"
],
"35": [
"Input_Bit_4",
"0",
"1",
"64",
false,
"0035",
"",
"3"
],
"36": [
"Input_Bit_5",
"0",
"1",
"64",
false,
"0036",
"",
"4"
],
"37": [
"Input_Bit_6",
"0",
"1",
"64",
false,
"0037",
"",
"5"
],
"38": [
"Input_Bit_7",
"0",
"1",
"64",
false,
"0038",
"",
"6"
],
"39": [
"Input_Bit_8",
"0",
"1",
"64",
false,
"0039",
"",
"7"
],
"40": [
"Input_Bit_9",
"0",
"1",
"64",
false,
"0040",
"",
"8"
],
"41": [
"Input_Bit_10",
"0",
"1",
"64",
false,
"0041",
"",
"9"
],
"42": [
"Input_Bit_11",
"0",
"1",
"64",
false,
"0042",
"",
"10"
],
"43": [
"Input_Bit_12",
"0",
"1",
"64",
false,
"0043",
"",
"11"
],
"44": [
"Input_Bit_13",
"0",
"1",
"64",
false,
"0044",
"",
"12"
],
"45": [
"Input_Bit_14",
"0",
"1",
"64",
false,
"0045",
"",
"13"
],
"46": [
"Input_Bit_15",
"0",
"1",
"64",
false,
"0046",
"",
"14"
],
"47": [
"Input_Bit_16",
"0",
"1",
"64",
false,
"0047",
"",
"15"
],
"48": [
"Input_Bit_17",
"0",
"1",
"64",
false,
"0048",
"",
"16"
],
"49": [
"Input_Bit_18",
"0",
"1",
"64",
false,
"0049",
"",
"17"
],
"50": [
"Input_Bit_19",
"0",
"1",
"64",
false,
"0050",
"",
"18"
],
"51": [
"Input_Bit_20",
"0",
"1",
"64",
false,
"0051",
"",
"19"
],
"52": [
"Input_Bit_21",
"0",
"1",
"64",
false,
"0052",
"",
"20"
],
"53": [
"Input_Bit_22",
"0",
"1",
"64",
false,
"0053",
"",
"21"
],
"54": [
"Input_Bit_23",
"0",
"1",
"64",
false,
"0054",
"",
"22"
],
"55": [
"Input_Bit_24",
"0",
"1",
"64",
false,
"0055",
"",
"23"
],
"56": [
"Input_Bit_25",
"0",
"1",
"64",
false,
"0056",
"",
"24"
],
"57": [
"Input_Bit_26",
"0",
"1",
"64",
false,
"0057",
"",
"25"
],
"58": [
"Input_Bit_27",
"0",
"1",
"64",
false,
"0058",
"",
"26"
],
"59": [
"Input_Bit_28",
"0",
"1",
"64",
false,
"0059",
"",
"27"
],
"60": [
"Input_Bit_29",
"0",
"1",
"64",
false,
"0060",
"",
"28"
],
"61": [
"Input_Bit_30",
"0",
"1",
"64",
false,
"0061",
"",
"29"
],
"62": [
"Input_Bit_31",
"0",
"1",
"64",
false,
"0062",
"",
"30"
],
"63": [
"Input_Bit_32",
"0",
"1",
"64",
false,
"0063",
"",
"31"
],
"64": [
"HEATER_V_STATUS",
"255",
"8",
"68",
false,
"0064",
"",
""
],
"65": [
"HEATER_I_STATUS",
"255",
"8",
"69",
false,
"0065",
"",
""
],
"66": [
"HEATER_P_STATUS",
"255",
"8",
"70",
false,
"0066",
"",
""
],
"67": [
"TEMP_PV_STATUS",
"255",
"8",
"71",
false,
"0067",
"",
""
],
"68": [
"TEMP_SET_PT_STATUS",
"255",
"8",
"72",
false,
"0068",
"",
""
],
"69": [
"FAN_V_STATUS",
"255",
"8",
"73",
false,
"0069",
"",
""
],
"70": [
"FAN_I_STATUS",
"255",
"8",
"74",
false,
"0070",
"",
""
],
"71": [
"FAN_P_STATUS",
"255",
"8",
"75",
false,
"0071",
"",
""
],
"72": [
"OVER_HEAT_STATUS",
"255",
"8",
"76",
false,
"0072",
"",
""
],
"73": [
"Modbus_Action_Status_10",
"255",
"8",
"77",
false,
"0073",
"",
""
],
"74": [
"Modbus_Action_Status_11",
"255",
"8",
"78",
false,
"0074",
"",
""
],
"75": [
"Modbus_Action_Status_12",
"255",
"8",
"79",
false,
"0075",
"",
""
],
"76": [
"Modbus_Action_Status_13",
"255",
"8",
"80",
false,
"0076",
"",
""
],
"77": [
"Modbus_Action_Status_14",
"255",
"8",
"81",
false,
"0077",
"",
""
],
"78": [
"Modbus_Action_Status_15",
"255",
"8",
"82",
false,
"0078",
"",
""
],
"79": [
"Modbus_Action_Status_16",
"255",
"8",
"83",
false,
"0079",
"",
""
],
"80": [
"Modbus_Action_Status_17",
"255",
"8",
"84",
false,
"0080",
"",
""
],
"81": [
"Modbus_Action_Status_18",
"255",
"8",
"85",
false,
"0081",
"",
""
],
"82": [
"Modbus_Action_Status_19",
"255",
"8",
"86",
false,
"0082",
"",
""
],
"83": [
"Modbus_Action_Status_20",
"255",
"8",
"87",
false,
"0083",
"",
""
],
"84": [
"Modbus_Action_Status_21",
"255",
"8",
"88",
false,
"0084",
"",
""
],
"85": [
"Modbus_Action_Status_22",
"255",
"8",
"89",
false,
"0085",
"",
""
],
"86": [
"Modbus_Action_Status_23",
"255",
"8",
"90",
false,
"0086",
"",
""
],
"87": [
"Modbus_Action_Status_24",
"255",
"8",
"91",
false,
"0087",
"",
""
],
"88": [
"Modbus_Action_Status_25",
"255",
"8",
"92",
false,
"0088",
"",
""
],
"89": [
"Modbus_Action_Status_26",
"255",
"8",
"93",
false,
"0089",
"",
""
],
"90": [
"Modbus_Action_Status_27",
"255",
"8",
"94",
false,
"0090",
"",
""
],
"91": [
"Modbus_Action_Status_28",
"255",
"8",
"95",
false,
"0091",
"",
""
],
"92": [
"Modbus_Action_Status_29",
"255",
"8",
"96",
false,
"0092",
"",
""
],
"93": [
"Modbus_Action_Status_30",
"255",
"8",
"97",
false,
"0093",
"",
""
],
"94": [
"Modbus_Action_Status_31",
"255",
"8",
"98",
false,
"0094",
"",
""
],
"95": [
"Modbus_Action_Status_32",
"255",
"8",
"99",
false,
"0095",
"",
""
],
"96": [
"Modbus_Master_Status",
"255",
"8",
"100",
false,
"0096",
"",
""
]
},
"out": {
"0": [
"Output_Word_1",
"0",
"16",
"101",
false,
"0097",
"",
""
],
"1": [
"Output_Word_2",
"0",
"16",
"103",
false,
"0098",
"",
""
],
"2": [
"Output_Word_3",
"0",
"16",
"105",
false,
"0099",
"",
""
],
"3": [
"Output_Word_4",
"0",
"16",
"107",
false,
"0100",
"",
""
],
"4": [
"Output_Word_5",
"0",
"16",
"109",
false,
"0101",
"",
""
],
"5": [
"Output_Word_6",
"0",
"16",
"111",
false,
"0102",
"",
""
],
"6": [
"Output_Word_7",
"0",
"16",
"113",
false,
"0103",
"",
""
],
"7": [
"Output_Word_8",
"0",
"16",
"115",
false,
"0104",
"",
""
],
"8": [
"Output_Word_9",
"0",
"16",
"117",
false,
"0105",
"",
""
],
"9": [
"Output_Word_10",
"0",
"16",
"119",
false,
"0106",
"",
""
],
"10": [
"Output_Word_11",
"0",
"16",
"121",
false,
"0107",
"",
""
],
"11": [
"Output_Word_12",
"0",
"16",
"123",
false,
"0108",
"",
""
],
"12": [
"Output_Word_13",
"0",
"16",
"125",
false,
"0109",
"",
""
],
"13": [
"Output_Word_14",
"0",
"16",
"127",
false,
"0110",
"",
""
],
"14": [
"Output_Word_15",
"0",
"16",
"129",
false,
"0111",
"",
""
],
"15": [
"Output_Word_16",
"0",
"16",
"131",
false,
"0112",
"",
""
],
"16": [
"Output_Word_17",
"0",
"16",
"133",
false,
"0113",
"",
""
],
"17": [
"Output_Word_18",
"0",
"16",
"135",
false,
"0114",
"",
""
],
"18": [
"Output_Word_19",
"0",
"16",
"137",
false,
"0115",
"",
""
],
"19": [
"Output_Word_20",
"0",
"16",
"139",
false,
"0116",
"",
""
],
"20": [
"Output_Word_21",
"0",
"16",
"141",
false,
"0117",
"",
""
],
"21": [
"Output_Word_22",
"0",
"16",
"143",
false,
"0118",
"",
""
],
"22": [
"Output_Word_23",
"0",
"16",
"145",
false,
"0119",
"",
""
],
"23": [
"Output_Word_24",
"0",
"16",
"147",
false,
"0120",
"",
""
],
"24": [
"Output_Word_25",
"0",
"16",
"149",
false,
"0121",
"",
""
],
"25": [
"Output_Word_26",
"0",
"16",
"151",
false,
"0122",
"",
""
],
"26": [
"Output_Word_27",
"0",
"16",
"153",
false,
"0123",
"",
""
],
"27": [
"Output_Word_28",
"0",
"16",
"155",
false,
"0124",
"",
""
],
"28": [
"Output_Word_29",
"0",
"16",
"157",
false,
"0125",
"",
""
],
"29": [
"Output_Word_30",
"0",
"16",
"159",
false,
"0126",
"",
""
],
"30": [
"Output_Word_31",
"0",
"16",
"161",
false,
"0127",
"",
""
],
"31": [
"Output_Word_32",
"0",
"16",
"163",
false,
"0128",
"",
""
],
"32": [
"Output_Bit_1",
"0",
"1",
"165",
false,
"0129",
"",
"0"
],
"33": [
"Output_Bit_2",
"0",
"1",
"165",
false,
"0130",
"",
"1"
],
"34": [
"Output_Bit_3",
"0",
"1",
"165",
false,
"0131",
"",
"2"
],
"35": [
"Output_Bit_4",
"0",
"1",
"165",
false,
"0132",
"",
"3"
],
"36": [
"Output_Bit_5",
"0",
"1",
"165",
false,
"0133",
"",
"4"
],
"37": [
"Output_Bit_6",
"0",
"1",
"165",
false,
"0134",
"",
"5"
],
"38": [
"Output_Bit_7",
"0",
"1",
"165",
false,
"0135",
"",
"6"
],
"39": [
"Output_Bit_8",
"0",
"1",
"165",
false,
"0136",
"",
"7"
],
"83": [
"TEMP_PV_STATUS_RESET",
"0",
"1",
"169",
false,
"0180",
"",
"3"
],
"84": [
"TEMP_SET_PT_STATUS_RESET",
"0",
"1",
"169",
false,
"0181",
"",
"4"
],
"85": [
"FAN_V_STATUS_RESET",
"0",
"1",
"169",
false,
"0182",
"",
"5"
],
"86": [
"FAN_I_STATUS_RESET",
"0",
"1",
"169",
false,
"0183",
"",
"6"
],
"87": [
"FAN_P_STATUS_RESET",
"0",
"1",
"169",
false,
"0184",
"",
"7"
],
"88": [
"OVER_HEAT_STATUS_RESET",
"0",
"1",
"169",
false,
"0185",
"",
"8"
],
"89": [
"Action_Status_Reset_10",
"0",
"1",
"169",
false,
"0186",
"",
"9"
],
"90": [
"Action_Status_Reset_11",
"0",
"1",
"169",
false,
"0187",
"",
"10"
],
"91": [
"Action_Status_Reset_12",
"0",
"1",
"169",
false,
"0188",
"",
"11"
],
"92": [
"Action_Status_Reset_13",
"0",
"1",
"169",
false,
"0189",
"",
"12"
],
"93": [
"Action_Status_Reset_14",
"0",
"1",
"169",
false,
"0190",
"",
"13"
],
"94": [
"Action_Status_Reset_15",
"0",
"1",
"169",
false,
"0191",
"",
"14"
],
"95": [
"Action_Status_Reset_16",
"0",
"1",
"169",
false,
"0192",
"",
"15"
],
"96": [
"Action_Status_Reset_17",
"0",
"1",
"169",
false,
"0193",
"",
"16"
],
"97": [
"Action_Status_Reset_18",
"0",
"1",
"169",
false,
"0194",
"",
"17"
],
"98": [
"Action_Status_Reset_19",
"0",
"1",
"169",
false,
"0195",
"",
"18"
],
"99": [
"Action_Status_Reset_20",
"0",
"1",
"169",
false,
"0196",
"",
"19"
],
"100": [
"Action_Status_Reset_21",
"0",
"1",
"169",
false,
"0197",
"",
"20"
],
"101": [
"Action_Status_Reset_22",
"0",
"1",
"169",
false,
"0198",
"",
"21"
],
"102": [
"Action_Status_Reset_23",
"0",
"1",
"169",
false,
"0199",
"",
"22"
],
"103": [
"Action_Status_Reset_24",
"0",
"1",
"169",
false,
"0200",
"",
"23"
],
"104": [
"Action_Status_Reset_25",
"0",
"1",
"169",
false,
"0201",
"",
"24"
],
"105": [
"Action_Status_Reset_26",
"0",
"1",
"169",
false,
"0202",
"",
"25"
],
"106": [
"Action_Status_Reset_27",
"0",
"1",
"169",
false,
"0203",
"",
"26"
],
"107": [
"Action_Status_Reset_28",
"0",
"1",
"169",
false,
"0204",
"",
"27"
],
"108": [
"Action_Status_Reset_29",
"0",
"1",
"169",
false,
"0205",
"",
"28"
],
"109": [
"Action_Status_Reset_30",
"0",
"1",
"169",
false,
"0206",
"",
"29"
],
"110": [
"Action_Status_Reset_31",
"0",
"1",
"169",
false,
"0207",
"",
"30"
],
"111": [
"Action_Status_Reset_32",
"0",
"1",
"169",
false,
"0208",
"",
"31"
],
"112": [
"Master_Status_Reset",
"0",
"8",
"173",
false,
"0209",
"",
""
]
},
"mem": {
"0": [
"device_path",
"/dev/ttyRS485",
"256",
"174",
false,
"0210",
"",
""
],
"1": [
"baud_rate",
"9600",
"32",
"208",
false,
"0211",
"",
""
],
"2": [
"parity",
"0",
"8",
"212",
false,
"0212",
"",
""
],
"3": [
"data_bits",
"8",
"8",
"213",
false,
"0213",
"",
""
],
"4": [
"stop_bits",
"1",
"8",
"214",
false,
"0214",
"",
""
]
},
"extend": {
"deviceMisc": {
"tbl_A_rowcount": "9",
"ModbusMasterStatus_ModbusRTUMaster_20180122_1_1": "Modbus_Master_Status",
"MasterStatusReset_ModbusRTUMaster_20180122_1_1": "Master_Status_Reset"
},
"data": {
"ActionId_01_ModbusRTUMaster_20180122_1_1": "1",
"SlaveAddress_01_ModbusRTUMaster_20180122_1_1": "4",
"SlaveIP_01_ModbusRTUMaster_20180122_1_1": "",
"SlavePort_01_ModbusRTUMaster_20180122_1_1": "",
"FunctionCode_01_ModbusRTUMaster_20180122_1_1": "4",
"RegisterAddress_01_ModbusRTUMaster_20180122_1_1": "1",
"QuantityOfRegisters_01_ModbusRTUMaster_20180122_1_1": "2",
"ActionInterval_01_ModbusRTUMaster_20180122_1_1": "1000",
"DeviceValue_01_ModbusRTUMaster_20180122_1_1": "HEATER_V_HB",
"ModbusActionStatus_01_ModbusRTUMaster_20180122_1_1": "HEATER_V_STATUS",
"ActionStatusReset_01_ModbusRTUMaster_20180122_1_1": "HEATER_V_STATUS_RESET",
"ActionId_02_ModbusRTUMaster_20180122_1_1": "2",
"SlaveAddress_02_ModbusRTUMaster_20180122_1_1": "4",
"SlaveIP_02_ModbusRTUMaster_20180122_1_1": "",
"SlavePort_02_ModbusRTUMaster_20180122_1_1": "",
"FunctionCode_02_ModbusRTUMaster_20180122_1_1": "4",
"RegisterAddress_02_ModbusRTUMaster_20180122_1_1": "13",
"QuantityOfRegisters_02_ModbusRTUMaster_20180122_1_1": "2",
"ActionInterval_02_ModbusRTUMaster_20180122_1_1": "1000",
"DeviceValue_02_ModbusRTUMaster_20180122_1_1": "HEATER_P_HB",
"ModbusActionStatus_02_ModbusRTUMaster_20180122_1_1": "HEATER_P_STATUS",
"ActionStatusReset_02_ModbusRTUMaster_20180122_1_1": "HEATER_P_STATUS_RESET",
"ActionId_03_ModbusRTUMaster_20180122_1_1": "3",
"SlaveAddress_03_ModbusRTUMaster_20180122_1_1": "4",
"SlaveIP_03_ModbusRTUMaster_20180122_1_1": "",
"SlavePort_03_ModbusRTUMaster_20180122_1_1": "",
"FunctionCode_03_ModbusRTUMaster_20180122_1_1": "4",
"RegisterAddress_03_ModbusRTUMaster_20180122_1_1": "7",
"QuantityOfRegisters_03_ModbusRTUMaster_20180122_1_1": "2",
"ActionInterval_03_ModbusRTUMaster_20180122_1_1": "1000",
"DeviceValue_03_ModbusRTUMaster_20180122_1_1": "HEATER_I_HB",
"ModbusActionStatus_03_ModbusRTUMaster_20180122_1_1": "HEATER_I_STATUS",
"ActionStatusReset_03_ModbusRTUMaster_20180122_1_1": "HEATER_I_STATUS_RESET",
"ActionId_04_ModbusRTUMaster_20180122_1_1": "4",
"SlaveAddress_04_ModbusRTUMaster_20180122_1_1": "3",
"SlaveIP_04_ModbusRTUMaster_20180122_1_1": "",
"SlavePort_04_ModbusRTUMaster_20180122_1_1": "",
"FunctionCode_04_ModbusRTUMaster_20180122_1_1": "3",
"RegisterAddress_04_ModbusRTUMaster_20180122_1_1": "1071",
"QuantityOfRegisters_04_ModbusRTUMaster_20180122_1_1": "1",
"ActionInterval_04_ModbusRTUMaster_20180122_1_1": "1000",
"DeviceValue_04_ModbusRTUMaster_20180122_1_1": "TEMP_PV",
"ModbusActionStatus_04_ModbusRTUMaster_20180122_1_1": "TEMP_PV_STATUS",
"ActionStatusReset_04_ModbusRTUMaster_20180122_1_1": "TEMP_PV_STATUS_RESET",
"ActionId_05_ModbusRTUMaster_20180122_1_1": "5",
"SlaveAddress_05_ModbusRTUMaster_20180122_1_1": "3",
"SlaveIP_05_ModbusRTUMaster_20180122_1_1": "",
"SlavePort_05_ModbusRTUMaster_20180122_1_1": "",
"FunctionCode_05_ModbusRTUMaster_20180122_1_1": "3",
"RegisterAddress_05_ModbusRTUMaster_20180122_1_1": "1201",
"QuantityOfRegisters_05_ModbusRTUMaster_20180122_1_1": "1",
"ActionInterval_05_ModbusRTUMaster_20180122_1_1": "1000",
"DeviceValue_05_ModbusRTUMaster_20180122_1_1": "TEMP_SET_PT",
"ModbusActionStatus_05_ModbusRTUMaster_20180122_1_1": "TEMP_SET_PT_STATUS",
"ActionStatusReset_05_ModbusRTUMaster_20180122_1_1": "TEMP_SET_PT_STATUS_RESET",
"ActionId_06_ModbusRTUMaster_20180122_1_1": "6",
"SlaveAddress_06_ModbusRTUMaster_20180122_1_1": "2",
"SlaveIP_06_ModbusRTUMaster_20180122_1_1": "",
"SlavePort_06_ModbusRTUMaster_20180122_1_1": "",
"FunctionCode_06_ModbusRTUMaster_20180122_1_1": "4",
"RegisterAddress_06_ModbusRTUMaster_20180122_1_1": "1",
"QuantityOfRegisters_06_ModbusRTUMaster_20180122_1_1": "2",
"ActionInterval_06_ModbusRTUMaster_20180122_1_1": "1000",
"DeviceValue_06_ModbusRTUMaster_20180122_1_1": "FAN_V_HB",
"ModbusActionStatus_06_ModbusRTUMaster_20180122_1_1": "FAN_V_STATUS",
"ActionStatusReset_06_ModbusRTUMaster_20180122_1_1": "FAN_V_STATUS_RESET",
"ActionId_07_ModbusRTUMaster_20180122_1_1": "7",
"SlaveAddress_07_ModbusRTUMaster_20180122_1_1": "2",
"SlaveIP_07_ModbusRTUMaster_20180122_1_1": "",
"SlavePort_07_ModbusRTUMaster_20180122_1_1": "",
"FunctionCode_07_ModbusRTUMaster_20180122_1_1": "4",
"RegisterAddress_07_ModbusRTUMaster_20180122_1_1": "13",
"QuantityOfRegisters_07_ModbusRTUMaster_20180122_1_1": "2",
"ActionInterval_07_ModbusRTUMaster_20180122_1_1": "1000",
"DeviceValue_07_ModbusRTUMaster_20180122_1_1": "FAN_P_HB",
"ModbusActionStatus_07_ModbusRTUMaster_20180122_1_1": "FAN_P_STATUS",
"ActionStatusReset_07_ModbusRTUMaster_20180122_1_1": "FAN_P_STATUS_RESET",
"ActionId_08_ModbusRTUMaster_20180122_1_1": "8",
"SlaveAddress_08_ModbusRTUMaster_20180122_1_1": "2",
"SlaveIP_08_ModbusRTUMaster_20180122_1_1": "",
"SlavePort_08_ModbusRTUMaster_20180122_1_1": "",
"FunctionCode_08_ModbusRTUMaster_20180122_1_1": "4",
"RegisterAddress_08_ModbusRTUMaster_20180122_1_1": "7",
"QuantityOfRegisters_08_ModbusRTUMaster_20180122_1_1": "2",
"ActionInterval_08_ModbusRTUMaster_20180122_1_1": "1000",
"DeviceValue_08_ModbusRTUMaster_20180122_1_1": "FAN_I_HB",
"ModbusActionStatus_08_ModbusRTUMaster_20180122_1_1": "FAN_I_STATUS",
"ActionStatusReset_08_ModbusRTUMaster_20180122_1_1": "FAN_I_STATUS_RESET",
"ActionId_09_ModbusRTUMaster_20180122_1_1": "9",
"SlaveAddress_09_ModbusRTUMaster_20180122_1_1": "5",
"SlaveIP_09_ModbusRTUMaster_20180122_1_1": "",
"SlavePort_09_ModbusRTUMaster_20180122_1_1": "",
"FunctionCode_09_ModbusRTUMaster_20180122_1_1": "3",
"RegisterAddress_09_ModbusRTUMaster_20180122_1_1": "1471",
"QuantityOfRegisters_09_ModbusRTUMaster_20180122_1_1": "1",
"ActionInterval_09_ModbusRTUMaster_20180122_1_1": "1000",
"DeviceValue_09_ModbusRTUMaster_20180122_1_1": "OVER_HEAT",
"ModbusActionStatus_09_ModbusRTUMaster_20180122_1_1": "OVER_HEAT_STATUS",
"ActionStatusReset_09_ModbusRTUMaster_20180122_1_1": "OVER_HEAT_STATUS_RESET"
}
}
}
],
"Connections": []
}