Page 1 of 1
Detect Addon module Connection Status - NodeRed
Posted: 03 Nov 2023, 06:35
by mitchellday06
Hi,
I was wondering if there is any type of module state detection for addon modules in NodeRed.
I have 2 x MIO an AIO and a DIO. I wanted to have checks to see if the state disconnects or errors, then to perform some logic.
Mitchell
Re: Detect Addon module Connection Status - NodeRed
Posted: 08 Nov 2023, 16:57
by stefanh
Hi ,
you can monitor the modules, but this is different depending on the modules.
Make sure that you have set up your hardware correctly in PiCtory as Start-Config. and that Node-RED & the Node-RED RevPi Nodes Server is activated in Webstatus.
For the DIO module you can evaluate the variable "PIN: Status", if the module is OK it will give you a 0, if it fails an 841. For the AIO, you can analyze a status for each individual input and output. The variables are called OutputStatus_1 & InputValue_1 and so on. Unfortunately, the MIO itself does not provide a status.
Thank you for your contribution here in the forum, we have some homework to do so that all modules provide uniform statuses with documented error codes in future.
Regards
Stefan
Suppport | KUNBUS
Re: Detect Addon module Connection Status - NodeRed
Posted: 29 Nov 2023, 05:07
by mitchellday06
So if I analyzed an analogue input on the AIO, it could return a fail purely because of that one input? So to know if it is the module, would have to return failed for all?