Hi,

In my Project, I am using RevPI Connect + and RevPI DIO module, I have a Node-Red and CodeSys application running in the hardware.

Since I have a CoDeSys, is it ok to configure the DIO's only in the Device Tree in the CoDeSys or it also requires configuring through PiCtory too ?

Note: Right now, my PiCtory looks empty. [ Please refer the attached image of PiCtory and Codesys for a better understanding]

1. Is there any configuration to be made at CoDeSys to Configure these DO as either ' Push-Pull or High-Side?

2. If Configuring the CoDeSys is sufficient then, the Output module configured as which mode and how can I Change it?
Your input is highly appreciated.

Best Regards,
Mani

Re: PiCtory & CoDeSys

Posted: 13 Oct 2022, 08:54
by u.biakoup
Hello Manikandan_pils,

please have a look here:

https://kunbus-gmbh.atlassian.net/wiki/ ... tware+FAQ | Can I use PiCtory and Codesys at the same time?
https://kunbus-gmbh.atlassian.net/servi ... 2680586265---> Push Pull
https://kunbus-gmbh.atlassian.net/servi ... 2680520754----> High Side

Best Regards

Ulrich Kouatang Biakoup | Technical Support

Re: PiCtory & CoDeSys

Posted: 26 Oct 2022, 15:52
by Manikandan_pilz
hi,
thanks for helping me out, still my Output are getting on with the 24VDC, I have checked all the wiring, it seems to be ok.
And I found, the RevPI status bits 0 and 1 are high in Codesys and as per the help file bit 1 says it's missing Pictory configuration missing.
As per the shared link, I presume the Codesys configuration overwrite the Pictory , hence ideally it must work,
I am not sure, where exactly I am making a mistake, it would be a great help me finding the solution for this.
Refer the attached images for better understanding.
help on Codesys and Pictory