RevPi Gateway PROFINET interface to RevPi Core

Posted: 04 Feb 2022, 10:00
by mrwinter
Hello,

can anyone tell me what the physical interface between the Gateway (PROFINET) and RevPi Core looks like?
Specifically, the aim is to isolate the Ethernet side from the PLC from security purposes, i.e. get data from the PLC without exposing it to the network that the RevPi is in.
Therefore, if the bridge between RevPi Core and PNIO Gateway were serial (and we could even strip out the Ethernet pins from the bridge), that would be great.

Re: RevPi Gateway PROFINET interface to RevPi Core

Posted: 04 Feb 2022, 12:00
by nicolaiB
Hi Mrwinter,

the Profinet side is connected via a gateway. The gateway consists of a ASIC for the Profinet and a uC for the piBridge communication. There is no direct ethernet communication between the piBridge and the fieldbus.
Hope this answers your question.

Nicolai

Re: RevPi Gateway PROFINET interface to RevPi Core

Posted: 04 Feb 2022, 15:54
by mrwinter
Hi Nicolai,
thanks for your reply.
The PiBridge has RS485, some sniffer pins and Ethernet as far as I know. Do you know which pins are used for communication with the gateway?
Are there any schematics for the PNIO gateway?

Re: RevPi Gateway PROFINET interface to RevPi Core

Posted: 04 Feb 2022, 17:27
by nicolaiB
Hi,

the gateway uses sniff pins for presence detection and ethernet (from uC to RevPi, not connected to PLC network) for the transfer of the process image. Unfortunately the schematics of the gateway aren't publicly available.

Nicolai