I have a question regarding the scale of data received from AIO module using RevPiModIO2. I have a sensor connected to the AIO module but no way to test the full scale of the sensor(no physical access to the sensor and the pi).
In pictory Input 1 is set as follow:
-Range: -10V/+10V
- Multiplier:1
-Divisor:1
-Offset:0
-ADC_DataRate:640Hz
And in python I am reading the value using rpi.io.InputValue_1() in cycleloop(100ms).
How the rpi.io.InputValue_1() is scaled exactly (8 bit,16bit,24bit) it really not clear for me? from what i understand, Its a 24bits ADC so it should give me the following result;
-10V->0
0V->2^23(8388608)
10V->2^24(16777216)
but that doesn't match with the data that I have...
Could somebody help me,please ,to better understand ?
Best regards,
Martin
AIO module scale
Moderator: RevPiModIO
- RevPiModIO
- KUNBUS
- Posts: 335
- Joined: 20 Jan 2017, 08:44
- Contact:
Hi Martin!
The AIO module will process the data internally and gives us the "real" value. So if you configure the Input for -10 to 10 V you will get the value in mV directly from the AIO module. So the range is -10000 - 10000.
So in the piControl bus is already a processed value from the AIO module and all programs (piTest, RevPiModIO and so on) will show the real, processed value.
Regards
Sven
The AIO module will process the data internally and gives us the "real" value. So if you configure the Input for -10 to 10 V you will get the value in mV directly from the AIO module. So the range is -10000 - 10000.
So in the piControl bus is already a processed value from the AIO module and all programs (piTest, RevPiModIO and so on) will show the real, processed value.
Regards
Sven
python3-RevPiModIO - https://revpimodio.org/ || Der RevPi ist das Beste, was passieren konnte!
Thank you very much for your answer! It's a shame that I figured out the answer just before you reply! That is what happens when you don't read properly the manual...:
Martin
Best RegardsThe initial values always lie in the unit mV or µA respectively.