What is the sampling rate of RevPi IO module?

Posted: 10 Aug 2020, 12:13
by huanghuapan
Our customers want to collect high frequency vibration signals and generate 10,000 data in one second. Can our RevPi IO module meet this sampling rate?

Re: What is the sampling rate of RevPi IO module?

Posted: 11 Aug 2020, 10:25
by dirk
Dear huanghuapan, The DIO Module is able to use counters with up to 4 KHz sample rate
and the RevPi Compact has digital IOs with a sampe rate of 125 us.
But 10.000 samples per second means 100 us sample rate.
So this is unfortunately still too slow to meet this requirement.
What kind of sensor or measuring application do the customers have in mind?

Re: What is the sampling rate of RevPi IO module?

Posted: 12 Aug 2020, 03:57
by huanghuapan
Customers use vibration sensors to monitor equipment vibration