Posted: 05 May 2020, 23:54
Hi Dirk and Kunbus Team,
We are considering purchasing several units from your site but I'm confused about what combination will work best for our application. We are developing a transmitter/HMI unit for our sensors and we are thinking to use your core and gateways in our transmitter that will be connected to external controllers. The transmitter should be able to do the following:
1. Our transmitter will be always in slave mode for the Modbus RTU protocol. Do you think we can use the RS-485 on the connect core and use that in a slave mode?
2. The transmitter will also be in slave mode for the Profibus protocol. Same question as 1. Should we consider buying an additional Profibus slave module? Do you think we can use the Rs-485 on the connect as the Modbus RTU port and add 1 gateway for the Profibus requirement?
3. How many gateways can we connect to the core or connect? In our case, we need to make sure we have provisions for Modbus RTU, Profibus, analog outputs (ideally 4 channels), analog inputs (ideally 4 channels), and 1 RJ 45 for OPC connection.
I look forward to your reply. Also, will it be possible to get the design/circuit diagrams for the Modbus RTU slave, Profibus slave, and analog I/O expansion modules?
Best,
Rohit
We are considering purchasing several units from your site but I'm confused about what combination will work best for our application. We are developing a transmitter/HMI unit for our sensors and we are thinking to use your core and gateways in our transmitter that will be connected to external controllers. The transmitter should be able to do the following:
1. Our transmitter will be always in slave mode for the Modbus RTU protocol. Do you think we can use the RS-485 on the connect core and use that in a slave mode?
2. The transmitter will also be in slave mode for the Profibus protocol. Same question as 1. Should we consider buying an additional Profibus slave module? Do you think we can use the Rs-485 on the connect as the Modbus RTU port and add 1 gateway for the Profibus requirement?
3. How many gateways can we connect to the core or connect? In our case, we need to make sure we have provisions for Modbus RTU, Profibus, analog outputs (ideally 4 channels), analog inputs (ideally 4 channels), and 1 RJ 45 for OPC connection.
I look forward to your reply. Also, will it be possible to get the design/circuit diagrams for the Modbus RTU slave, Profibus slave, and analog I/O expansion modules?
Best,
Rohit