DO module: Detecting open load
Posted: 28 Mar 2020, 00:13
by aharrah
The page describing the I/O modules mentions:
Each output can additionally be configured to detect open load conditions when in high side switch mode and send an alarm to RevPi Core.
How do I read or get notified of the alarm when there is an open load condition?
Thanks,
Andy
Re: DO module: Detecting open load
Posted: 01 Apr 2020, 12:33
by dirk
Hi aharrah,
you have to read out the variable "OutputOpenLoadDetect", i.e. by "piTest -r <variable>".
Have a look at this tutorial
How to Configure Digital I/O Modules
Re: DO module: Detecting open load
Posted: 01 Apr 2020, 17:05
by aharrah
That page had some good information on it.
After configuring OutputOpenLoadDetection how do I check to see if there is an open load on an output?
In digging a little bit I did come across this page:
https://revolution.kunbus.com/tutorials ... iguration/ which includes the following:
OutputOpenLoadDetection has not yet been put into practice.
Is this a still a true statement?
Thanks,
Andy
Re: DO module: Detecting open load
Posted: 30 Jun 2020, 16:34
by dirk
Hi Andy, we have updated our documentation. The feature is working and the description how is available here:
https://revolution.kunbus.com/tutorials ... iguration/
Re: DO module: Detecting open load
Posted: 22 Jul 2024, 16:49
by cerberus78
Can you please show step by step for this point ?
i didn't manage to get the status. The status is always 0... when is should get some data
Re: DO module: Detecting open load
Posted: 31 Jul 2024, 15:30
by cerberus78
i have configured OutputOpenLoadDetect with value 255 so that i have the status of the 8 first outputs
but how to read the status ?
Regards
Re: DO module: Detecting open load
Posted: 02 Aug 2024, 16:13
by dirk
Hi cerberus78, it is the variable "Output_Status" which indicates a broken cable for the activated channels.
Here is a practical example in case you want to monitor a broken cable on output 1 using a 24V LED:
- Connect a 24V led on output 1 and switch on via "piTest -w O_1,1"
- DIO LED Output 1
- Configure open load detection for output channel 1:
Don't forget to do the two steps in the PiCtory menu afterward: "File → Save as standard configuration" and "Tools → Reset driver"
- Continuously read the status of the outputs
Code: Select all
piTest -r Output_Status
2 Byte-Value of Output_Status: 0 dez (=0000 hex)
2 Byte-Value of Output_Status: 0 dez (=0000 hex)
...
- Then switch off the LED connection - here I just did it by removing the GND connection:
- DIO LED Switch of
- Continuously read the status - it changed to 1 which indicates the open load detection on channel 1
Code: Select all
piTest -r Output_Status
2 Byte-Value of Output_Status: 1 dez (=0001 hex)
2 Byte-Value of Output_Status: 1 dez (=0001 hex)
2 Byte-Value of Output_Status: 1 dez (=0001 hex)
...
Re: DO module: Detecting open load
Posted: 19 Aug 2024, 11:17
by cerberus78
Thank you !!
Re: DO module: Detecting open load
Posted: 09 Sep 2024, 16:29
by cerberus78
after testing it is not as expected
what i wanted to do is to detect if an output is disconnected or not
the ouput can state can be on or off.
with the configuration you showed me we consider that output is always on
is there a way to do this case ?
Re: DO module: Detecting open load
Posted: 10 Sep 2024, 17:07
by dirk
No, unfortunately. You need to have a load to detect an open load and thus some electricity flowing through a cable.