We need to interface some Digital input and Digital Output with RevPi Device.
Our Requirement is as follows:
1. DI-55 /DO-19 / AI -46 / AO-19

Following calculation we made
12 RevPi AIO =48 AI and 24 AO (Not considering the RTD input )
4 RevPi DIO=56 DI and 56 DO
So 12 AIO +4DIO =16 expansion modules.
Case 1. If we use the RevPi connect then to attach the 16 expansion modules we required 4 RevPi Connect.
Case 2.if we use the RevPi core then to attach the 16 expansion modules we need 2 RevPi Core.

My question is, are the above calculations feasible? (As we have limitation for expansion modules)

Also, can we use some kind of Remote I/o systems that will connect to all the i/o signals and give inputs in Modbus TCP. (We are referring TB20 modules from Helmholz).Then Modbus TCP to RevPi device.

Re: Interfacing of AIO/DIO/DO/DI with RevPi Connect and RevPi Core

Posted: 23 Sep 2019, 11:00
by dirk
Dear Anil, the RevPi Core modules have 2 PiBridges. The RevPi Connect Modules have one PiBridge and one Con Bridge

Each PiBridge can take
  • Up to 5 IO Modules (DI/DO/DIO)
  • Up to one module may be exchanged by a RevPi Gate Module or an AIO Module