Common Earth or Seperate

Post by h2oil »

Is it ok to Earth the AIO module along with the RevPi Connect on same earth as a 220-24VDC transformer?

Just want to check no signal noise for mA reading will be made

Thanks :)
User avatar
dirk
KUNBUS
Posts: 2174
Joined: 15 Dec 2016, 13:19

Re: Common Earth or Seperate

Post by dirk »

Hi h2oil, this is a question that I have to ask in the hardware department.
User avatar
dirk
KUNBUS
Posts: 2174
Joined: 15 Dec 2016, 13:19

Re: Common Earth or Seperate

Post by dirk »

Hi, to make it short - you can use a common ground for the AIO and your power supply. It depends on your measuerement accuracy requirements. In case you want mV accuracy the line resistance i.e. may be involved here.