Can I use multiple Modbus RTU masters to control one slave?

Topics about the Software of Revolution Pi
Post Reply
AyKay
Posts: 5
Joined: 05 Mar 2019, 12:25

Can I use multiple Modbus RTU masters to control one slave?

Post by AyKay »

I have two pressure controllers (Bronkhorst EL-Press) wired using Modbus RTU as slaves. I have configured a Virtual Modbus RTU Master in Pictory. My problem is that in order to control both slaves, I need to use more commands than the maximum 32 inputs that Pictory allows for coils and holding registers.
Can I use more than one Modbus RTU Master to control the slaves?
User avatar
dirk
KUNBUS
Posts: 2174
Joined: 15 Dec 2016, 13:19

Re: Can I use multiple Modbus RTU masters to control one slave?

Post by dirk »

Hello AyKay, there is a Virtual Device in PiCtory called Modbus RTU Master 150 which has 150 registers. In general you may use more than one Modbus RTU master. But more than one master to one slave could lead to some collissions.
AyKay
Posts: 5
Joined: 05 Mar 2019, 12:25

Re: Can I use multiple Modbus RTU masters to control one slave?

Post by AyKay »

Hallo Dirk. Thanks for your response. I followed your suggestion and used the RTU150 Master. Unfortunately, I am still encountering the 32 limitation (please see attached photo).
Extended_data.jpg
Extended_data.jpg (570.29 KiB) Viewed 5567 times