Hello, I'm working on a project with a RevPI Connect, I'm using it to drive a JVL MOTOR Mac800 (by MODBUS TCP).
I implemented a TCP Master in Pictory. And I wrote my own C++ code to get RevPi var.. (using piTest example)..
My project was working properly with my old configuration (RevPI Core 3).
Now I did the same thing with my RevPI Connect, but ........ impossible to get it work.
On my JVL Motor => there is a LED that shows is MODBUS connection is OK, and => it's ok.. (green led).
It's seems that the MODBUS TCP MASTER on revpi does not work because variables are all empty (0).
Here is the output of a simple program, (only for debug purpose) ==>
Found 4 devices:
Address: 0 module type: 105 (0x69) unknown moduletype V1.0
Module is present
input offset: 202 length: 6
output offset: 208 length: 5
Address: 31 module type: 96 (0x60) RevPi DIO V1.3
Module is present
input offset: 89 length: 70
output offset: 159 length: 18
Address: 30 module type: 103 (0x67) RevPi AIO V1.3
Module is present
input offset: 0 length: 20
output offset: 20 length: 4
Address: 64 module type: 24579 (0x6003) ModbusTCP Master Adapter V0.0
Module is present
input offset: 213 length: 101
output offset: 314 length: 73
Modbus_Master_Status : 0x00 0x02
Modbus_Action_Status_1 : 0x03 0xff
Modbus_Action_Status_2 : 0xff 0xff
Modbus_Action_Status_3 : 0xff 0xff
Modbus_Action_Status_4 : 0xff 0xff
Modbus_Action_Status_5 : 0xff 0xff
Modbus_Action_Status_6 : 0xff 0xff
Modbus_Action_Status_7 : 0xff 0xff
Modbus_Action_Status_8 : 0xff 0xff
Modbus_Action_Status_9 : 0xff 0xff
Modbus_Action_Status_10 : 0xff 0xff
Modbus_Action_Status_11 : 0xff 0xff
Modbus_Action_Status_12 : 0xff 0xff
Modbus_Action_Status_13 : 0xff 0xff
Modbus_Action_Status_14 : 0xff 0xff
Modbus_Action_Status_15 : 0xff 0xff
Modbus_Action_Status_16 : 0xff 0xff
Modbus_Action_Status_17 : 0xff 0xff
Modbus_Action_Status_18 : 0xff 0xff
Modbus_Action_Status_19 : 0xff 0xff
Modbus_Action_Status_20 : 0xff 0xff
Modbus_Action_Status_21 : 0xff 0xff
Modbus_Action_Status_22 : 0xff 0xff
Modbus_Action_Status_23 : 0xff 0xff
Modbus_Action_Status_24 : 0xff 0xff
Modbus_Action_Status_25 : 0xff 0xff
Modbus_Action_Status_26 : 0xff 0xff
Modbus_Action_Status_27 : 0xff 0xff
Modbus_Action_Status_28 : 0xff 0xff
Modbus_Action_Status_29 : 0xff 0xff
Modbus_Action_Status_30 : 0xff 0xff
Modbus_Action_Status_31 : 0xff 0xff
Modbus_Action_Status_32 : 0xff 0x00
As you can see there is the value 0x02 in Modbus_Master_Status... But this value is not documented here ==> https://revolution.kunbus.com/tutorials ... verwenden/
You can see too that there is ==> Modbus_Action_Status_1 : 0x03 0xff
I cannot understand why....
Could you help me ?
MODBUS TCP MASTER with RevPI Connect
Re: MODBUS TCP MASTER with RevPI Connect
Hi, the RevPi Connect is not configured.
It should look similar like this
Update your configuration in PiCtory again. Consider to upgrade your system as there is a new Stretch image available in the shop.
Code: Select all
Address: 0 module type: 105 (0x69) unknown moduletype V1.0
Code: Select all
Address: 0 module type: 105 (0x69) RevPi Connect V1.0