Failed to Read Modbus RTU Master

Show the world your Revolution Pi project!
Post Reply
Anam
Posts: 1
Joined: 11 Oct 2024, 15:08

Failed to Read Modbus RTU Master

Post by Anam »

I have trouble modbus rtu master setting on the Revolution Pi Connect S. After setting modbus master in pictory it won't show the output or input. Using RevPi for modbus master, and VSD ATV-320 for modbus slave. Trying to connect directly to a pc using VSD ATV-320 it can already. Why is using RevPi problematic in modbus connection? I have connected it to another modbus slave such as TK4S, it also works.
Online
User avatar
dirk
KUNBUS
Posts: 2132
Joined: 15 Dec 2016, 13:19

Re: Failed to Read Modbus RTU Master

Post by dirk »

Hello Anam,
Please use the steps in this helpful checklist to check whether the physical connection is correctly assembled:
RS-485 Checklist

If this works, then you are not far away from Modbus communication. Then take the steps from this checklist and check whether the setup is correct:
Modbus Checklist

I can also recommend this video tutorial - Modbus RTU Master:
https://revolutionpi.com/en/tutorials/video-tutorials
Post Reply