Hello!
I have connected RevPi Core SE, DIO, and MIO. However, if I change the parameters for MIO, they are not changed, and there is no voltage on the output. For example, if I have default settings for MIO and want to change AnalogOutput_1, I change it, reading the value directly after it. It shows that it has not changed (picture). The DIO is working correctly by the way. I checked it for two different MIO modules, but the same problem. So I guess the problem is somewhere in the Core module. I hope you have some ideas on how to repair it.
Thanks!
RevPi MIO is not working correctly
RevPi MIO is not working correctly
- Attachments
-
- 2.JPG (35.59 KiB) Viewed 7941 times
-
- 1.JPG (123.49 KiB) Viewed 7941 times
Re: RevPi MIO is not working correctly
Hello limpopo, okay so there seams to be a problem using the MIO module analogue output. Let's take a look at it together.
First, the documentation is here: https://revolutionpi.com/tutorials/anal ... gurieren-2
These are the steps to configure the MIO module accordingly
- AnalogOutputMode1 = analog Output
- AnalogOutput 1 = Set the output voltage here. The value must be between 0 and 10000 and is stated in mV.
The whole configuration parameters are here Can you check your configuration according to these parameters?
Can you verify that there are no other tasks that overwrite that parameter "AnalogOutput_1"?
First, the documentation is here: https://revolutionpi.com/tutorials/anal ... gurieren-2
These are the steps to configure the MIO module accordingly
- AnalogOutputMode1 = analog Output
- AnalogOutput 1 = Set the output voltage here. The value must be between 0 and 10000 and is stated in mV.
The whole configuration parameters are here Can you check your configuration according to these parameters?
Can you verify that there are no other tasks that overwrite that parameter "AnalogOutput_1"?
Re: RevPi MIO is not working correctly
Thanks!
But I got where there was a problem, the problem was in PiCtory version. I updated PiCtory and after that, MIO stopped working. I had 2.0.7-1+revpi10+3 version, then I wrote this command: sudo apt install pictory=2.0.6 .
Everything began to work again.
But I got where there was a problem, the problem was in PiCtory version. I updated PiCtory and after that, MIO stopped working. I had 2.0.7-1+revpi10+3 version, then I wrote this command: sudo apt install pictory=2.0.6 .
Everything began to work again.
Re: RevPi MIO is not working correctly
Hello limpopo, Thank you for your positive response.